We are having a kitchen re fit. We are fitting 2x electric ovens in a housing unit. These are both 13amp with 2.8kw. Our electrician has said they can go on our current kitchen circuit (with the dishwasher, fridge and kettle) Would this be sensible, or should we be having a separate circuit for the ovens put in?
 
There is a recommendation (not a regulation) that fixed appliances rated at 2kW or more should be supplied by their own dedicated circuit, so it would be far from sensible.
The two ovens in the same unit could arguably be considered one appliance and fed by one circuit with two 13A fused isolators at the appliance end, or they could be fed by two separate smaller rated circuits.
 