Hi all when connecting to the metal clad backboxes that have a powder coat finish how do you remove the paint so that any metal connection - bushes or couplers or washers are earth bonded with the socket?
 
It depends on what purpose the connection is for and also the specification for a particular job.

Some specifications (old-fashioned theses days I guess) will call for hats and jaggies regardless.

If the connection to the conduit, gland etc is as a CPC then I'd lean towards using an earthing nut these days.

If it is just to earth the conduit then I would do this at the earth terminals in BESA boxes on the conduit system rather than relying on the termination to painted back boxes.

If it's conduits connected into a galv trunking system then the connection at the trunking end should suffice.
 