Hi guys, I'm pretty new at testing and I started work a few months ago working on outdoor advertising units and bus shelters (please don't laugh)
Anyway I'm trying to figure out supply types for when we test installations, now the stuff I work on (50% of it) is fed from a service pillar on the pavement and the dno cutout supply (cable going into) is SWA (meaning it is a spur from nearby street lighting which can be isolated in the street lamp column). The other 50% of sites are fed from underground dno supply cables (jointed in ground), it is these cables I need to know how to identify the supply type. Currently I'm told to put it down as pme, and if its a SWA feed then put down tncs or tns accordingly (no sites have TT supply that I have come across).
Is this correct?
From previous readings on this forum, all pme supply's are tncs but not all tncs are pme?

My fingers are sore from excessive head scratching, I suppose the language barrier at work doesn't help (me being a mancunion (gods best creation) and the others being scoucers lol)
 
god created mancs as a first attempt. after sorting out all the faults, he then created scousers. note the spelling.
 
as fot the electrical bits.... get your dog to pi$$ on it. if he jumps up 2 ft., it's TN=S. any higher, it's PME. :smilielol5::smilielol5:
 
god created mancs as a first attempt. after sorting out all the faults, he then created scousers. After a bit more snagging he got the design perfect. Then he made Geordies
Aaawww Tel, I didn't know you cared :)
 
From previous readings on this forum, all pme supply's are tncs but not all tncs are pme?


It could be PNB instead of PME, but both are TN-C-S.

I would advise getting hold of a copy of Guidance note 8 mate. It has diagrams of the various earthing arrangements. :)
 