J
Jimmyb
hello ppl, I'm installing a pool heater at home, it is a 15ft round metal frame pool but after last year and the 3 kW heater and having to have it on 10 hours before you got in i decided to buy a 15 kw one.
I have now just got round to installing it, the heater is a 5meter run to heater, I know i need to put an earth rod in as the supply is tncs but after asking a few mates, they said "all so connect supply earth" can someone please tell me the right way as i thought not to connect.
Thanks in advance.:confused:
if you are taking a supply from your house to another cu then connect the earth at the house end but do not connect at the other end. You should run a 16mm earth to an earth rod at the new cu end. this will give the cable the protection it needs and will prevent a fault on the heater tripping out breakers in the house. or the rcd at the front of the board in the house. if there is one.
The cable from the house should be an swa 10mm to carry the current drawn by the heater if it is 15kw.
hi willospark, no it a farm i live on where the main power comes into a building with switched fuses ect then from there, around the farm to sheds including the house so my supply will be coming off that building.
i will running 16mm meter tails from the service head into a csu with 30ma RCD and 80 amp MCB then from there 3 x 16mm singles in trucking to heater
I was installing a earth rod as supply was tncs but was told it was ok to use supply earth and if id like then put a rod in for safety but i also thought this wasn't allowed
I would read carefully any and all manufacturers instructions that come with the heater.....personally I would be "TT"ing the the heater myself. It just eliminates the risk of any PD arising between the pool itself and the general mass of earth.
I think the esqcr regs prohibit this.