Problem

I've ran a 110v supply from the opposite panel off a different tranny and the fault was still present
 
What's the rating of the transformer(s) and what's the rating of the control cct fuses?
 
Sounds like a short down or duff coil etc dragging voltage down ...maintain power to control circuit but isolate all L1/L2/L3 at all contactors and drop the loads off - a few ways to trace and attack this problem you can isolate all through power and disconnect each contactor coil and put a known 110 across each one see if they operate ok... I would follow the start stop circuits and see control order as you are not switching any loads you won't bugger the motor up.

The fault has to be close to the origin of the control whichever contactors pull in first or even relays as it does it on the start option anything brought in after is not a suspect.
 
4amp fuse for the controll cct
Don't remember the rating of the tranny but it's the same model In the panel next to it
 
Are the affected 'rattling' contactors the ones with the pneumatic timers attached if so have you checked that contacts are 'clean' and that timings are reasonably accurate? (Both these tasks can be checked with the panel isolated from all supplies - dead testing)
EDIT
Is it a dusty environment?
 
Dark wood there's a test key switch on the panel I've been testing it that way with just the control cct being live :)
Best things ever installed on a panel for fault finding if you have the key that is :)
I wasn't overly keen in pressing the start button in a lot and firing a lower voltage through the coils incase I start burning them out so I was doing a fair bit of dead testing , I've been getting roughly 120 ohms across most of the coils
Think I'll be doing the wandering 110v lead on Friday but I have a feeling the fault isn't in my panel.
The only external stuff I know of is an nrv/check valve with limit switches on it and there's a wee auto lube pump
 
As you haven't mentioned a smell of burning from the panel I have assumed that there are no 'shorting' coils dragging the supply down so I still think the problem lies with a 'dirty' contact or two! I would be testing the contacts on those timers along with any retaining contacts as there could be a few of those too.
 
I wish I had been able to tell work “I’m going home now I’ll sort the effluent pumps out Friday”.

Other than testing the voltage on a lamp what else have you done?

PS what do all the other timers do?
 
I'm sure you could have told them that Tony, that is of course assuming you wanted to be in the job centre by Friday? ;)
 
Fast&rough, please let us know how you get on this Friday, it will make a refreshing change to receive feedback from the original posters from time to time, it should also help others in the future when they come to use the search function.
 
Staggered start
Start delay
Star/delta changeover
Cant remember what the others are for
And they have another 3 pumps to choose from
Any yeah I'll fix it tomorrow if I don't I'll no be back on here haha
 
May have been mentioned before.
Are the contactor coils DC if so a faulty rectifier on the control circuit supply would cause this.
 
That's us sorted
Faulty core from nrv interlock which is also an add on
managed to find a set of drawings

6ahesu6y.jpg
3yseryry.jpg
bapuzeze.jpg
 