Sorry 5544. You beat me to it !
well assuming it has pump over run, then the pump will stay on long enough to get the system below the required temp, normally about 5 mins. In honesty it takes some going to blow a fuse on a central heating system. Normal suspects would be the fan or the pump. the only other areas would be a failure of the elcetronics, but then, you would expect that they would not work again once re energised making it easy to detect.
if you look up the operation of a three port valve on the internet (sorry im too thick to add it to this), and find a good schematic then it becomes clearer how the system works. as previously stated, the tank state is really a simple switch and rarely goes wrong. the good thing is that fault finding on these systems is easier since you can break it down to external controls or boiler quite simply.