New build, customer (who is builder) supplied light fittings.
With the darker mornings builder asked if I could get the lights working. So made it safe and put it on a 13A plug and plugged into the site board.
Before energising obviously did some testing and noticed that insulation resistance was low (0.45M). Went on to investigate and found that it was 3 light fittings. They were 'on' and each was giving an insulation resistance of about 1.5M - even confirmed that with one of them fully disconnected. Anyway left the lights on temporarily.
Made some inquiries with the manufacturers and they come back that insulation resistance should be at least 2M, but ordinarily should be a lot higher.
Went back this week and re-tested, to identify defective lights for replacement and now the insulation resistance is way up (+100M).
I can only think that there may have been some dampness in the light fittings.
Any other ideas?
With the darker mornings builder asked if I could get the lights working. So made it safe and put it on a 13A plug and plugged into the site board.
Before energising obviously did some testing and noticed that insulation resistance was low (0.45M). Went on to investigate and found that it was 3 light fittings. They were 'on' and each was giving an insulation resistance of about 1.5M - even confirmed that with one of them fully disconnected. Anyway left the lights on temporarily.
Made some inquiries with the manufacturers and they come back that insulation resistance should be at least 2M, but ordinarily should be a lot higher.
Went back this week and re-tested, to identify defective lights for replacement and now the insulation resistance is way up (+100M).
I can only think that there may have been some dampness in the light fittings.
Any other ideas?