glad to see its not just me who refers to it as pyro! " OOOW DONT U MEAN MINAERAL INSULATED CABLE" no i mean pyro u snotty little ####! he probably wouldn,t know what pyro was if you hit him with it!lol

Don't think there is anything ''Snotty'' about calling it MICC, it's more to do with how you were taught and what it was being called in your local surroundings than anything else!! I can remember being told during my training that Pyro is just a shortened term for ''Protenex'' which is just one of several manufactures producing MICC, and the term shouldn't be used a cable description. But then everyone and his dog in the industry, knows what your talking about when you refer to Pyro! ...lol!! MICC has just stuck with me, rather than Pyro! ..lol!!
 
Being a year out of college I can 100% certain guarantee that we were not shown how to pot Pyro because and I quote the head of department of my college "It is outdated and you should be using FP200" the closet we got to Pyro was our tutor hitting it with a hammer to demonstrate its indestructibility of the cable after calling the head of apartment several curse words for saying pyro is outdated and it is better to use FP200,
Unfortunately I have no experience with Pyro and would love to learn how to work with it, its due to the course requirements I did do a course with C&G but was not taught Pyro.
 
Anyone that thinks FP200 type cables can replace MICC in every instance, is a certified fool!!

I get more disillusioned with these modern day collage and training center lecturers, every time i hear this kind of inappropriate, ill informed personal preference crap!!
 
One enduring memory of pyro was placing a piece connected to a megger over the anvil and smacking 7 bells out of it. It held up until the edge of the hammer caught it.

Unfortunately under M&Q regs we weren’t allowed to use it.
 
Don't think there is anything ''Snotty'' about calling it MICC, it's more to do with how you were taught and what it was being called in your local surroundings than anything else!! I can remember being told during my training that Pyro is just a shortened term for ''Protenex'' which is just one of several manufactures producing MICC, and the term shouldn't be used a cable description. But then everyone and his dog in the industry, knows what your talking about when you refer to Pyro! ...lol!! MICC has just stuck with me, rather than Pyro! ..lol!!

I assume you mean "Pyrotenax" (why is there no technical spell checker) which was the name of the original manufacturer of the cable. As well as MICC it is sometimes referred to as MIMS
 
I'm working for a LA and they also say it should be rewired, I do generally find very poor IR readings on the installations though.

Yet the 40+ year old communal lighting installations all seem ok?

Does anyone know why this is? Does bare pyro not like being buried in plaster/screed?
 
I think that bare unsheathed pyro buried in cement could be a problem with the copper being attacked by whatever is in the cement.

Used to call it either Pyro or MIMS round my way.

Yooj
 
I'm working for a LA and they also say it should be rewired, I do generally find very poor IR readings on the installations though.

Yet the 40+ year old communal lighting installations all seem ok?

Does anyone know why this is? Does bare pyro not like being buried in plaster/screed?

I think that bare unsheathed pyro buried in cement could be a problem with the copper being attacked by whatever is in the cement.

Like copper pipe really, if MICC is going to be directly laid in or through concrete, cement, render etc it should be sheathed, protective coated, or run in a PVC containment in case there is an element in those substances that reacts with copper. Most poor IR readings are down to badly made off pot's, rarely the copper sheath!!

I wouldn't take much creed in any LA Engineer, i've always found them to be mostly ''failed'' Engineers from the real world of contracting/consultancy. LA's are usually the last hope for all failed disipline Engineers, especially road Traffic Engineers, i'm sure you've all seen examples of there bright ideas in your areas!! ...lol!!
 
It's not quite dead yet.

The last 2 big fire alarm jobs I've done (new hospitals) were both done in MI, I for one really enjoy working with it and would use it more if cost permitted.
 
Im going to check it out next weekend so i will let you guys know the fault, according to the old PIR i did, it had the lowest IR reading of all the circuits so i will check it out again.
 
Being a year out of college I can 100% certain guarantee that we were not shown how to pot Pyro because and I quote the head of department of my college "It is outdated and you should be using FP200"
He's probably only saying that because he was useless at making it off and dressing it properly when he was a spark in the real world
 
He's probably only saying that because he was useless at making it off and dressing it properly when he was a spark in the real world

the thing with fp and its variants,its a hell of a job to make it look good, but done right pyro comes of the reel straight as a die and is much easier to dress,bit harder if working outside in the cold but still better to install than fp
 
FP 200 is a poor man's replacement for MICC. I replaced FP warped by the sun on a factory roof a while ago. No chance of that with MICC. I mentioned, in an earlier post, that the only problem I have found was with small, three phase, induction motors. I think BICC were the cable manufacturers. Quite a problem occurred, due to inverse eddy currents. Surge arresters were provided but were incorrect. There were some very loud bangs. One cable, embedded in a group of about twenty on cable tray, was down. Not worth replacing, so added another cable and disconnected the damaged one (didn't fancy ripping it out and redressing that lot).
 