Piratepete

Hi Guys.
Doing a CU change.
Found a supply to the swimming pool pump shed done in orange Pyro. The cable is clipped along the outside of the house and then disappears underground reappearing in the shed.

I know nothing about Pyro.

1. Is it allowable to use it this way (instead of armoured)? If not, should I condemn it? Insulation between cores is good > 500Meg.

2. How can I work out the current rating? The end is potted and has tails printed 1.0/1.5 sqmm. Can I tell from the diameter?

Cheers
Pete
 
Hi Guys.
Doing a CU change.
Found a supply to the swimming pool pump shed done in orange Pyro. The cable is clipped along the outside of the house and then disappears underground reappearing in the shed.

I know nothing about Pyro.

1. Is it allowable to use it this way (instead of armoured)? If not, should I condemn it? Insulation between cores is good > 500Meg.

2. How can I work out the current rating? The end is potted and has tails printed 1.0/1.5 sqmm. Can I tell from the diameter?

Cheers
Pete

If you dont know 2. You are not competant.

It tells you in the bgb everything you neef for 2.

Its the last two ccc tables if I remember correctly
 
Hi Guys.
Doing a CU change.
Found a supply to the swimming pool pump shed done in orange Pyro. The cable is clipped along the outside of the house and then disappears underground reappearing in the shed.

I know nothing about Pyro.

1. Is it allowable to use it this way (instead of armoured)? If not, should I condemn it? Insulation between cores is good > 500Meg.

2. How can I work out the current rating? The end is potted and has tails printed 1.0/1.5 sqmm. Can I tell from the diameter?

Cheers
Pete

Why do you feel the need to condemn it the IR is good

To find the cable size look at the gland it will be stamped with the number of cores, duty and core csa eg 2L1.5 or 2H1.5 alternatively if you know the cable diameter use this Info table to look up what you need to know
 
I didn't realise it could be used underground as a substitute for SWA. Just used to only seeing it in fire applications, I suppose. Thanks again for the guidance on ID and rating.

Not just fire alarms Pete.

Back in the day whole factories and foundries were wired with it and when it's done right it looks very impressive and is virtually indestructible.
 
Not just fire alarms Pete.

Back in the day whole factories and foundries were wired with it and when it's done right it looks very impressive and is virtually indestructible.

I assume it's not used much now for industrial applications? I think that to many of us DIs, Pyro's a forgotten and mysterious world!
 
I assume it's not used much now for industrial applications? I think that to many of us DIs, Pyro's a forgotten and mysterious world!

It's been a long time since I saw any new stuff and I'm not sure if it's still available but I stand to be corrected.

My dad was chief engineer in a chemical plant and all the wiring was Pyro. It was a dangerous place with lots of inflammable fumes around and it often caught fire, but the Pyro always managed to survive.

The place was so dangerous that the Labour Exchange (now called Job Centre) blackballed it and refused to send anybody to work there.
 
It's been a long time since I saw any new stuff and I'm not sure if it's still available but I stand to be corrected.
It is still available Geordie, it's just that the stuff is so bloody expensive everybody specs FP. When you compare them pyro is far and away the better kit. Apparently it's back on the syllabus for apprentices now too which is a good thing in my opinion.
 
It is still available Geordie, it's just that the stuff is so bloody expensive everybody specs FP. When you compare them pyro is far and away the better kit. Apparently it's back on the syllabus for apprentices now too which is a good thing in my opinion.

Thanks for that.

I've never worked with it - just worked in places where it was installed - but being an engineer (of the mechanical type) I was able to recognise good gear when I saw it.
 
It's been a long time since I saw any new stuff and I'm not sure if it's still available but I stand to be corrected.

My dad was chief engineer in a chemical plant and all the wiring was Pyro. It was a dangerous place with lots of inflammable fumes around and it often caught fire, but the Pyro always managed to survive.

The place was so dangerous that the Labour Exchange (now called Job Centre) blackballed it and refused to send anybody to work there.

We all know you are dangerous. It runs in the family then?

Pyro is fantastic stuff, I put a length on an anvil and set to with a hammer. It took a fair few hits with a hammer to get the IR to start breaking down.

Its one fault is underground if the outer PVC sheath gets damaged. Some acidic soils will eventually rot the copper sheath and it will go down. That said, it’ll put up with more abuse than an SWA.

As has been said, “if it ain’t broke, don’t fix it!”
 
We all know you are dangerous. It runs in the family then?

Pyro is fantastic stuff, I put a length on an anvil and set to with a hammer. It took a fair few hits with a hammer to get the IR to start breaking down.

Its one fault is underground if the outer PVC sheath gets damaged. Some acidic soils will eventually rot the copper sheath and it will go down. That said, it’ll put up with more abuse than an SWA.

As has been said, “if it ain’t broke, don’t fix it!”

The only slight downside I can think of is in the ground a pyro won't stand up to a shovel quite as well as a SWA.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Pyro Underground!?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
44
Unsolved
--

Advert

Thread statistics

Created
Piratepete,
Last reply from
Guest111,
Replies
44
Views
6,944

Advert

Back
Top