Try gently warming the last 6 or 7 inches of the MI towards the gland, being that old damp may have crept in, if the reading increases as you heat up the MI then sure as eggs is eggs its damp
 
Crickey, perhaps Friday night isn't the best time to be asking questions on here. I have a di-log tester and have learnt to take it's insulation resistance readings with a pinch of salt. I seriously think the mineral insulation was stopping the IR test from being performed. Going back to my original question, would you say 68 ohms is normal for neutral/earth on pyro or have I just been given duff info.
The info you have been given is correct, i would expect to see those kind of results on pyro or any other type of cable for that matter, that has seen better days. :smile5:
 
don't think damp could get it down to 68ohms.
 
So when I put my mft on IR test and connect it it also shows 0 volts l-n 0 volts l-e and 0 volts n-e but it puts out between 250 to 1000 volts depending upon the setting,is it knackered or do I need some of that powdered stuff out of the pyro to make it work properly? lol:smile5::smile5::smile5::smile5:
 
Thank you, more helpful responses! I am not too concerned about the insulation resistance readings at the moment as I suspect the door bell transformer may be spurred off of the same pyro somewhere and still connected. I was always taught to do the continuity test before Insulation resistance and as I'm getting 68 ohms between neutral and earth, I know a insulation resistance test will never be successful. What through me was the 68 ohms between neutral and earth...Yet the line and earth was >200 ohms. Don't know why my older and more expereinced electrician said this is normal on pyro?

- - - Updated - - -

So when I put my mft on IR test and connect it it also shows 0 volts l-n 0 volts l-e and 0 volts n-e but it puts out between 250 to 1000 volts depending upon the setting,is it knackered or do I need some of that powdered stuff out of the pyro to make it work properly? lol:smile5::smile5::smile5::smile5:

Not so much that one.
 
So when I put my mft on IR test and connect it it also shows 0 volts l-n 0 volts l-e and 0 volts n-e but it puts out between 250 to 1000 volts depending upon the setting,is it knackered or do I need some of that powdered stuff out of the pyro to make it work properly? lol:smile5::smile5::smile5::smile5:


lol - :44:
 
Thank you, more helpful responses! I am not too concerned about the insulation resistance readings at the moment as I suspect the door bell transformer may be spurred off of the same pyro somewhere and still connected. I was always taught to do the continuity test before Insulation resistance and as I'm getting 68 ohms between neutral and earth, I know a insulation resistance test will never be successful. What through me was the 68 ohms between neutral and earth...Yet the line and earth was >200 ohms. Don't know why my older and more expereinced electrician said this is normal on pyro?

- - - Updated - - -



Not so much that one.
if it was damp in the cable then linking L and N and testing both to earth would prove this without risking damage to anything left on,however if this is a feed to a cu then why would a bell transformer be connected to it,surely that should be on a fuse in the cu?
 
Thank you, more helpful responses! I am not too concerned about the insulation resistance readings at the moment as I suspect the door bell transformer may be spurred off of the same pyro somewhere and still connected. I was always taught to do the continuity test before Insulation resistance and as I'm getting 68 ohms between neutral and earth, I know a insulation resistance test will never be successful. What through me was the 68 ohms between neutral and earth...Yet the line and earth was >200 ohms. Don't know why my older and more expereinced electrician said this is normal on pyro?

- - - Updated - - -



Not so much that one.
Definetely not normal on pyro, as others have said.
 
if it was damp in the cable then linking L and N and testing both to earth would prove this without risking damage to anything left on,however if this is a feed to a cu then why would a bell transformer be connected to it,surely that should be on a fuse in the cu?

I suspect the pyro may be feeding another small 2 way c.u. for the communual lighting and door but can't check due to lack of access. Surely that is beside the point though, if I'm getting 68 ohms neutral earth does that not demonstrate the cable needs replacing anyway and my older electrcian is playing silly buggers..

As a side note, real shame that this forum seems to be going down the pan. Being taken over by sarky and smart !ss contributors. Was so helpful when I completed my 2391. Such a shame...
 
I left the room as it were out of shear embarrassment, think again about what you're asking, as pointed out as far as conductors go it's just another cable, what if you had the same readings on a 2 core swa cable, would you be asking the same question?

That is not what I was asking. I was asking if 68 ohms neutral earth on Pyro was normal, perhaps it was/is connected to some tncs system.
 
I suspect the pyro may be feeding another small 2 way c.u. for the communual lighting and door but can't check due to lack of access. Surely that is beside the point though, if I'm getting 68 ohms neutral earth does that not demonstrate the cable needs replacing anyway and my older electrcian is playing silly buggers..

As a side note, real shame that this forum seems to be going down the pan. Being taken over by sarky and smart !ss contributors. Was so helpful when I completed my 2391. Such a shame...
it's not being sarky when you say your megger was showing 0 volts across all connections and so wouldn't test,it won't work if it picks up a voltage on these,as a safety feature,or did they not teach you that on your 2391?
 
I suspect the pyro may be feeding another small 2 way c.u. for the communual lighting and door but can't check due to lack of access. Surely that is beside the point though, if I'm getting 68 ohms neutral earth does that not demonstrate the cable needs replacing anyway and my older electrcian is playing silly buggers..


Untill you can prove you are testing just the Pyro with nothing else connected to it, any readings you have obtained are meaningless.
 
I suspect the pyro may be feeding another small 2 way c.u. for the communual lighting and door but can't check due to lack of access. Surely that is beside the point though, if I'm getting 68 ohms neutral earth does that not demonstrate the cable needs replacing anyway and my older electrcian is playing silly buggers..

As a side note, real shame that this forum seems to be going down the pan. Being taken over by sarky and smart !ss contributors. Was so helpful when I completed my 2391. Such a shame...

Are you saying that you're trying to test a cable without disconnecting it from some other DB? How do you know where the fault is if you haven't isolated it from other equipment?

Edit: I see that snowhead got there first!
 