I agree with snowhead, you really need disconnect any loads and do a proper 500 volt insulation resistance test between all conductors to truly determine what condition the pyro is in.
 
it's not being sarky when you say your megger was showing 0 volts across all connections and so wouldn't test,it won't work if it picks up a voltage on these,as a safety feature,or did they not teach you that on your 2391?

Yes they did. But 90% of the time my Di log tester has shown 0 volts it's because there's been something interfering with the results. Surely, I shouldn't be getting a reading between neutral and earth.
 
Yes they did. But 90% of the time my Di log tester has shown 0 volts it's because there's been something interfering with the results. Surely, I shouldn't be getting a reading between neutral and earth.

but until you do the full range of tests with both ends isolated , then you cant confirm that it is actually the cable causing any fault.........?

dont make me use the facepalm poster.
 
The neutral earth reading may be being picked up threw a connected load mate,,,,, isolate and re-test
 
using continuity tests as means of finding faults between cores isnt worth a crap anyway as it lacks the "energy force" that a insulation resistance test current provides.

i'll stop talking now.*
lol







* yeah , you wish.
:-)
 
With 30 years experience as claimed on your website, u must know by now how to perform the correct tests?
 
if this is a feed cable,and it's still connected at both ends the neutral earth reading could be down to the suppliers earth,think about it.
 
I suspect the pyro may be feeding another small 2 way c.u. for the communual lighting and door but can't check due to lack of access. Surely that is beside the point though, if I'm getting 68 ohms neutral earth does that not demonstrate the cable needs replacing anyway and my older electrcian is playing silly buggers..

As a side note, real shame that this forum seems to be going down the pan. Being taken over by sarky and smart !ss contributors. Was so helpful when I completed my 2391. Such a shame...

I can only think you were asking sensible questions when you did the 2391 which is errrr an inspection and testing qualification and now you come on here with this question and don't expect some sarky comments

Yes they did. But 90% of the time my Di log tester has shown 0 volts it's because there's been something interfering with the results. Surely, I shouldn't be getting a reading between neutral and earth.

Are you sure it isn't the user that is causing problems with the results if it isn't I suggest you bin the meter and get one that is more reliable
 
i got there ages ago when i said he should be testing it with both ends dissed.
 
Crickey, perhaps Friday night isn't the best time to be asking questions on here. I have a di-log tester and have learnt to take it's insulation resistance readings with a pinch of salt. I seriously think the mineral insulation was stopping the IR test from being performed. Going back to my original question, would you say 68 ohms is normal for neutral/earth on pyro or have I just been given duff info.
so...have you got a callibration cert to go with it?

or is it a case of stick down some plausable values on the SOT....such as 199.9M for a newly installed cable....
 
Swifters you need to undertake an insulation resistance test of the MI, that will tell you if moisture has got in causing insulation breakdown.

When you say the MI has been disconnected I'm assuming all conductors have been pulled, as in neutral and earth?
 
45 posts with mine to sort out the most basic of tests. If you don’t trust your meter what’s the point of testing?
You can’t beat the old method. The bang test, beats any meter hands down!
 