dazza1981
I agree with snowhead, you really need disconnect any loads and do a proper 500 volt insulation resistance test between all conductors to truly determine what condition the pyro is in.
it's not being sarky when you say your megger was showing 0 volts across all connections and so wouldn't test,it won't work if it picks up a voltage on these,as a safety feature,or did they not teach you that on your 2391?
Yes they did. But 90% of the time my Di log tester has shown 0 volts it's because there's been something interfering with the results. Surely, I shouldn't be getting a reading between neutral and earth.

I suspect the pyro may be feeding another small 2 way c.u. for the communual lighting and door but can't check due to lack of access. Surely that is beside the point though, if I'm getting 68 ohms neutral earth does that not demonstrate the cable needs replacing anyway and my older electrcian is playing silly buggers..
As a side note, real shame that this forum seems to be going down the pan. Being taken over by sarky and smart !ss contributors. Was so helpful when I completed my 2391. Such a shame...
Yes they did. But 90% of the time my Di log tester has shown 0 volts it's because there's been something interfering with the results. Surely, I shouldn't be getting a reading between neutral and earth.
so...have you got a callibration cert to go with it?Crickey, perhaps Friday night isn't the best time to be asking questions on here. I have a di-log tester and have learnt to take it's insulation resistance readings with a pinch of salt. I seriously think the mineral insulation was stopping the IR test from being performed. Going back to my original question, would you say 68 ohms is normal for neutral/earth on pyro or have I just been given duff info.
i got there ages ago when i said he should be testing it with both ends dissed.