Diconnect both ends and whack a 1000 volts down it with your IR tester, where are you? I could come down or up wherever you are and sort it out for you, I still have all my pyro kit and although it is old I reckon I can sort the problem out for you without pulling in a new armoured.
 
Tbh, I think you've all been a bit harsh with the OP here. I understood his #1 in a different light....My Metrel tells you the voltage it got to before achieving a resistance to measure on an IR...instant fail = 0v. At that point, I too would probably have done a continuity test instead to get a meaningful value. Yes, he needs to make sure it's completely dis'd to be meaningful, but asking on here because he doubts something he's been told is entirely appropriate I'd have thought. I can't remember the last time that I touched some pyro so if an old hand made a comment that contradicted what I thought to be true it would probably have me in a moment of self-doubt, too.
 
I have seen this type of thing so many times now with pyro it is unbelievable, You may find removing the black cap which is crimped into the pot and then removing the compound may help if a pot is down. Pull the cables with a pair of pliers and get a blow lamp on the end, then add new compound into the pot and re-fit the cap. Now admittedly it is 50/50 whether the damage done will be too much to reuse but worth a shot as if you are careful you may get away with it, My first reaction would be to completely disconnect both ends and whack a 1000 volts down as mentioned to see if the reading alters at all, it may well be you have a tncs system there and the neutral to earth reading normal as they are linked anyhow at the DNO side, if you have not isolated all circuits via a double pole switch then it will be expected. I Would then suggest if still down and no reaction from the 1000 volts to try to examine the cable run if possible, again if no damage apparent try the pot work I suggested carefully. What size is the pyro? it will say on the pot, a long shot But I may have one, I have all types of bits and bobs in my store and there are some imperial glands in there I know, is it a L or H pot, I have some Hs but limited on the Ls.
 
Most sizes of imperial cable can be re-sealed with a metric pot give or take a bit of reaming or soldering to mount it securely on the sheath. But first...

68Ω is a funny resistance to be a cable fault. It's too high to be a solid short circuit, if copper touches copper so lightly that the resistance is that high I'd expect it to be variable and probably change from one test to another. OTOH it's too low to be moisture, even if you soaked the cable end in a bucket I doubt it would drop below a kΩ.

My money is on a fault on a final or load connected to this presumed extra DB, or that the cable has been damaged somewhere and suffered a power arc that has vapourised a lot of copper and blown itself clear leaving a general splattering of copper across the insulant.

Clearly, you need to isolate the cable completely and re-test. As others have said, pyro is just cable and it works like any other, the readings should be exactly as you would expect for SWA except that there's more of a chance, if the work was poorly carried out or something has got damaged, that the IR will come up low. Low IR on pyro is just as much a fault as on SWA.
 
Thank you, more helpful responses! I am not too concerned about the insulation resistance readings at the moment as I suspect the door bell transformer may be spurred off of the same pyro somewhere and still connected. I was always taught to do the continuity test before Insulation resistance and as I'm getting 68 ohms between neutral and earth, I know a insulation resistance test will never be successful. What through me was the 68 ohms between neutral and earth...Yet the line and earth was >200 ohms. Don't know why my older and more expereinced electrician said this is normal on pyro?

- - - Updated - - -



Not so much that one.
Don't know where you got that info from, if MI is made off correctly then you should expect a perfect IR reading. The reason why sometimes you don't is a badly made off termination, every MI that I terminated was IR tested as soon as the glands were connected to the enclosure/box, what ever. I'm sure your cable has an ingress of damp, due probably to a poorly made off termination. MI is/was used in all sorts of conditions including wet conditions.
 