I have seen this type of thing so many times now with pyro it is unbelievable, You may find removing the black cap which is crimped into the pot and then removing the compound may help if a pot is down. Pull the cables with a pair of pliers and get a blow lamp on the end, then add new compound into the pot and re-fit the cap. Now admittedly it is 50/50 whether the damage done will be too much to reuse but worth a shot as if you are careful you may get away with it, My first reaction would be to completely disconnect both ends and whack a 1000 volts down as mentioned to see if the reading alters at all, it may well be you have a tncs system there and the neutral to earth reading normal as they are linked anyhow at the DNO side, if you have not isolated all circuits via a double pole switch then it will be expected. I Would then suggest if still down and no reaction from the 1000 volts to try to examine the cable run if possible, again if no damage apparent try the pot work I suggested carefully. What size is the pyro? it will say on the pot, a long shot But I may have one, I have all types of bits and bobs in my store and there are some imperial glands in there I know, is it a L or H pot, I have some Hs but limited on the Ls.