Discuss Questionable Conductor Size in the Industrial Electricians' Talk area at ElectriciansForums.net
As you'll soon be in a position to test the resistance there's little point doing what I was going to suggest which was to cut the ends of an offcut carefully square, measure the length, strip the insulation, weigh the copper and determine the CSA from the density.
A 70mm² solid conductor is only 9.44mm diameter and the ideal compacted conductor is as close to this as possible. Datasheets for a couple of 50mm² terminals give the cable socket ID as 9.6 and 10mm respectively, so it is theoretically possible for a compacted 70mm² to fit a 50mm² lug, although I too am surprised it fits that easily.
I've noticed a trend for compacted conductors getting to be an increasingly sloppy fit in lugs, it doesn't inspire confidence.
I always ask for correct lugs to be supplied with a cable wherever possible, yet still they turn up loose.
We were supplied with some 10mm hybrid cable (fibre in the same sheath) and very few 10mm crimps fit correctly, turned out it was 8 AWG cable from China.
Reply to Questionable Conductor Size in the Industrial Electricians' Talk area at ElectriciansForums.net
Hi, just want to check something. I am on a facility which has a 4 core 70mm non armoured feed from the transformer, coming into the DB at the...
I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I...
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...