nah, that's sultans and sultanas. sulphates are more spread
 
Last edited:
Might do that after I've changed the CU on Monday!!
aye but insist that its no good for continued service.....as we`v just had the runround from a DNO over an earth issue...both this and that should be a priority for em....hmm we`l see....lol...
 
Nobody mentioned it and I thought maybe the word was out of fashion or superseded and no longer used.
 
Not being able to identify the rating of the fuse is not a limitation. A limitation is an agreement between the test engineer and the person ordering the work as to what will not be tested and inspected and the reason why.

I.E you cant isolate a circuit because it is needed to power a life support machine etc etc. This would be noted as a limitation on the PIR sheet.

Cheers............Howard
 
i would put N/V if i could not verify thre fuse type and rating.
 
Hi Howard, how and where would you record the fact that the main fuse cannot be identified then?
 
1361 60A is my guess as my house runs on exactly the same piece of tosh on the first cut out which then feeds an 80A BS88 cracking bit of discrimination!
 
1361 60A is my guess as my house runs on exactly the same piece of tosh on the first cut out which then feeds an 80A BS88 cracking bit of discrimination!
On and industrial install i did the DNO fitted the same rated fuses as my 200Amp BS88 (type 2) but was told discrimination wasnt lost as he had fitted type 4's..... not sure if this happens in domestic though or whether it actually does achieve discrimination in a fault.
 
On and industrial install i did the DNO fitted the same rated fuses as my 200Amp BS88 (type 2) but was told discrimination wasnt lost as he had fitted type 4's..... not sure if this happens in domestic though or whether it actually does achieve discrimination in a fault.


they know mine is wrong as they are changing it on the 7th of next month! why would you put one cut out feeding another!
 
they know mine is wrong as they are changing it on the 7th of next month! why would you put one cut out feeding another!
Industrial 3phase main 200A isolator feeding busbar fed from their ISU, you have to have independant fusing when supplying 3phase and cant rely on DNO fuses unlike domestic where DNO fuse protect accumulative load of all circuits from overload of your dist board.
 
Industrial 3phase main 200A isolator feeding busbar fed from their ISU, you have to have independant fusing when supplying 3phase and cant rely on DNO fuses unlike domestic where DNO fuse protect accumulative load of all circuits from overload of your dist board.
I'm talking domestic here hence "my house"
 