can i wire a 6mm from a old wirlex board 32a fuseway to a rcd in 6 mm then ring circuit into rcd
 
yes chris its something i did about 1o years ago ment to replace fuseboard at a later date it a 6 way wirlex put a rcd unit next to board and wired a 6 mm to rcd just wondered if it ok on regs i am a industrial electrisian for 35 years never did house wiring now retired age 53 on pension son looking at jobs i should have done
 
Yes its perfectly acceptable IMO, seen it loads of times, especially in industrial situations with old boards for which rcbo's are not available, infact I have seen 1 DB with about 15 of them, you would think it may have been easier/cheaper to replace DB... until you seen the bunch of pyros going into it from all angles!
 
can i wire a 6mm from a old wirlex board 32a fuseway to a rcd in 6 mm then ring circuit into rcd

Nothing wrong with that!! But if your talking about your own property, surely as a retired electrician with time on your hands, it'll be better to replace the old non RCD protected CU with one that has. One that is of a suitable size, to accommodate all your circuit needs
 
look at it again got 2 spare way in cu 2 lighting 2 ring main and looks in good condition it would plobly mean extending meter tails breaking seals so thinking if it still ok regs wise and been in for ten years i just need to tidy with clips cables going into cu
 