My first post because this just lay on my mind i decided to ask the experts.
First of all I am not an electrician, i am not even a DIY electrician, I work in building maintenance which mainly involves refurb (turnover) of apartments. I don't mess with electrics although my job may require me to change a lightbulb or the odd fuse. I leave the electrics to the professionals.
We had a fire in one of the apartments and as you can imagine there was lots of smoke damage and water damage from the sprinklers going off. After the fire the fire department ripped out the cooker hood and other appliances that were basically charcoal it was determined that the apartment would need a full refurb and as it was an insurance job, external contractors were sent in to refit a new kitchen, new floor, replaster etc etc. It was nothing to do with me or my colleague as we are busy with other move in and move outs.
Two months on my manager asks me to nip up and have a look as building concierge reported water coming from under the door indicating a leak (something we deal with all the time) however this time we knew this apartment was unoccupied and nearly in completion with a new kitchen fitted etc etc. I entered and discovered someone had turned the water on despite the kitchen tap tails not even connected up. Turns out an appliance guy had come and fitted the dishwasher and washing machine the day before and (he or who knows) left one of the tap tail isolators slightly cracked open despite not being connected. I was surprised to see under the sink was an exposed wire that is is usually where the socket for the dishwasher would be, almost submerged in the water the leak generated, I also noticed the all the MCB's were on as well as the RCD all switched up. Naturally i assumed this was not connected up to the circuit otherwise the RCD would just trip. Or so i thought. My colleague came up and said that might be live. I said how can it. Nothing has tripped. He hovered his voltage pen near it. It was definitely live.
We Isolated the consumer unit and got electricians in. This was careless work somewhere down the line but my confusion is that i thought the RCD would cause an unearthed unconnected circuit to trip. Clearly i don't understand this but it would be nice if i did.
My first post because this just lay on my mind i decided to ask the experts.
First of all I am not an electrician, i am not even a DIY electrician, I work in building maintenance which mainly involves refurb (turnover) of apartments. I don't mess with electrics although my job may require me to change a lightbulb or the odd fuse. I leave the electrics to the professionals.
We had a fire in one of the apartments and as you can imagine there was lots of smoke damage and water damage from the sprinklers going off. After the fire the fire department ripped out the cooker hood and other appliances that were basically charcoal it was determined that the apartment would need a full refurb and as it was an insurance job, external contractors were sent in to refit a new kitchen, new floor, replaster etc etc. It was nothing to do with me or my colleague as we are busy with other move in and move outs.
Two months on my manager asks me to nip up and have a look as building concierge reported water coming from under the door indicating a leak (something we deal with all the time) however this time we knew this apartment was unoccupied and nearly in completion with a new kitchen fitted etc etc. I entered and discovered someone had turned the water on despite the kitchen tap tails not even connected up. Turns out an appliance guy had come and fitted the dishwasher and washing machine the day before and (he or who knows) left one of the tap tail isolators slightly cracked open despite not being connected. I was surprised to see under the sink was an exposed wire that is is usually where the socket for the dishwasher would be, almost submerged in the water the leak generated, I also noticed the all the MCB's were on as well as the RCD all switched up. Naturally i assumed this was not connected up to the circuit otherwise the RCD would just trip. Or so i thought. My colleague came up and said that might be live. I said how can it. Nothing has tripped. He hovered his voltage pen near it. It was definitely live.
We Isolated the consumer unit and got electricians in. This was careless work somewhere down the line but my confusion is that i thought the RCD would cause an unearthed unconnected circuit to trip. Clearly i don't understand this but it would be nice if i did.