RCD TRipping

Hi
Have a RCD tripping, was just sat near the kitchen where the CU is and heard a trip in the fuse cupboard, 32A Down stairs sockets, only for sockets, fridge, cooker , heating off te other half of split load.
Have removed all plugs and switched off sockets and taken wires out of the furthest socket, removed one live from the mcb, still tripping, changed then round for the other live, still tripping.
Any other things I can try ?.

cheers
Scot
 
Hi
Have a RCD tripping, was just sat near the kitchen where the CU is and heard a trip in the fuse cupboard, 32A Down stairs sockets, only for sockets, fridge, cooker , heating off te other half of split load.
Have removed all plugs and switched off sockets and taken wires out of the furthest socket, removed one live from the mcb, still tripping, changed then round for the other live, still tripping.
Any other things I can try ?.

cheers
Scot
Just Removed both Neutrals and it still trips, removed both cpc's and it dose not trip , it cpc will trip on each earth connected !
 
Removing the cpcs on a live circuit is not the greatest of ideas it is dangerous.
 
standard set of tests required.
insulation resistance on all the circuits will normally find the issue.
however, the fast way 80% of the time is to disconnect anything related to outside.
outside lights, outside heaters, hot tubs, fancy garden lights, wall lights etc.
after that it is in order of likeyhood
oven
immersion heater
fridge/freezer
 