RCD type for heat pump

I'm fitting a heat pump tomorrow, not seen it yet and I don't usually get involved with stuff like this or solar/ev etc. cant be bothered by it all. But I'm doing it as a favour for someone as a one off. I've not seen the job yet, so do all heat pumps need a type B RCD or is it a case of read the instructions, if I do need a type B, where the hell do you get them from, its a hager RCBO board, quite new I think and the only type B RCD that shows up in a google search is a £200 4 module wide thing, single phase though. Do they not make RCBO's with type B characteristics (note not the curve, the actual RCD side of things.)

 
I note my inverter for solar panels stipulates a type AC RCD, so need to read the instructions.
 
Hmm, instructions were a waste of time, the only bits I could see were these snippets.

The ground fault circuit interrupter must be a C type breaker of 30 mA(<0.1s). Failure to do so may cause electrical shock.

Do they even make a type C RCD? thought it went AC - A - F - B in terms of protection. C probably mean the tripping curve.

It also says this.

When installing the ground fault circuit interrupter make sure that it is compatible with the inverter (resistant to high frequency electrical noise) to avoid unnecessary opening of the ground fault circuit interrupter.

That means nothing to me.


The installer was pretty clueless as well. Crazy how everyone has to go on multi thousand pound courses to do anything these days and at the end of them they are still as clueless as they were before the course.
 
I'm fitting a heat pump tomorrow, not seen it yet and I don't usually get involved with stuff like this or solar/ev etc. cant be bothered by it all. But I'm doing it as a favour for someone as a one off. I've not seen the job yet, so do all heat pumps need a type B RCD or is it a case of read the instructions, if I do need a type B, where the hell do you get them from, its a hager RCBO board, quite new I think and the only type B RCD that shows up in a google search is a £200 4 module wide thing, single phase though. Do they not make RCBO's with type B characteristics (note not the curve, the actual RCD side of things.)

You will definitely need to read the manufacturers instructions. Some heat pumps (Vaillant) require a type B RCD, but NOT a standard type B, they need the type B that westward has linked you. A normal type B is only rated up to 1000hz whereas the inverter on the vaillant heat pumps can go up to 20000hz (which an HP type B RCD can handle).
 
The type C is your trip curve and that will be the protective device at the consumer unit. You then run through the RCD I have linked in #2, this is not an RCBO.
Heat pumps contain VFDs and will produce DC components therefore it must not be connected through any other RCDs which are A or AC in the installation.
 
BS7671 does not specify RCDs for heat pumps but the manufacturer almost certainly will do.
 
You will definitely need to read the manufacturers instructions. Some heat pumps (Vaillant) require a type B RCD, but NOT a standard type B, they need the type B that westward has linked you. A normal type B is only rated up to 1000hz whereas the inverter on the vaillant heat pumps can go up to 20000hz (which an HP type B RCD can handle).
The background to the Hager/ Vaillant "HP" version of rcd is revealed in the amusing article here:
I think it became an essential requirement in the installation instructions only last year (or maybe year before)

I suspect it only really matters when you also have solar and battery inverters creating a cacophony of EMI, perhaps together with a DC component.
 
Last edited:
Am I the only one thinking the equipment design is at fault if it’s spewing that much noise into the mains ? What happened to standards about that sort of thing ?
 
So what do you do when the instructions are gobbledygook then, I've linked to the instructions for the model I wired up above, if anyone can find the correct information in there then be my guest.
 
This isn't difficult there is a lot of info online regarding heat pumps and suitable RCDs. #2, #5 and #6 of this thread gives you all the info you need.
 
I know this may sound like heresy, but if it's installed with the right cable and method, could you just omit the RCD and run it from an MCB ?
 
I know this may sound like heresy, but if it's installed with the right cable and method, could you just omit the RCD and run it from an MCB
This is fine and in accordance with BS7671 but manufacturers of these pumps nearly always state an RCD.
 