Thats an interesting thought - thanks for that. That would get my paperwork sorted, but I suppose it is a bit of a fudge, as the underlying problem still exists.When one is stuck with multiple RCDs for whatever reason, it is possible to test only the downstream RCD without risk of tripping the upstream one, by connecting the earth lead of the tester to the neutral on the line side of the RCD under test. This returns the test current to the circuit so that the upstream device does not see an imbalance.
Since my original post, I actually have a dual rcd board that I took out from another job which could be adapted to solve this issue.