If the RCD works, I'd get on with it and get out of there!
If it doesn't, this is one where you could easily open a large can of worms that I'd personally choose to keep shut. It would be a rather challenging CU change if it turns out to be required. (Inset CU and looks like conduit for CPC). It's fairly likely the 100ma RCD is for fault protection of a TT system, or maybe it was TT once and is now PME.
I'd do a Zs@DB (remembering there could be parallel paths). If inconclusive I'd test local incoming earth (disconnected) with main switch off .
If I got higher that TNS numbers back I wouldn't get involved beyond advising in writing to customer that the fault protection of their installation couldn't be confirmed and more work is needed to investigate and rectify.
If it doesn't, this is one where you could easily open a large can of worms that I'd personally choose to keep shut. It would be a rather challenging CU change if it turns out to be required. (Inset CU and looks like conduit for CPC). It's fairly likely the 100ma RCD is for fault protection of a TT system, or maybe it was TT once and is now PME.