doing eicr report on property.they have 16 mm twin and 10 mm earth feeding flat on house with its on seperate 100 amp pme supply.cable connects straight into supply via isolator(din rail type) there is no fuse.it feeds a 8.5 kw shower,2 kw water heater,six 2 kw panel heaters,electric cooker,2 kw fan heater in bathroom and socket circuit and 2 light circuits.if that wasnt anoth a 50 amp 16mm swa then feeds a studio that has 2 or 3 2 kw heaters and sockets and lights.they say been installed 10 years and never a problem.might be when i fit 60 amp switch fuse at source.was thinking of reducing power by putting contactors and timers so only limited load at any one time on 2 kw heaters and water heating.any good ideas?
 
I'm marginally cheaper at ZAR2500.00/hr but my travel can bump up the cost as well.

Seriously it's a hell of a jump from doing an EICR to installing load shedding. There's a few steps in between like applying diversity or testing the maximum demand etc.

You might get away with an 80Amp fuse on a 16mm cable but check the tables in your local regs. Even if you install a 60A fuse it's unlikely to blow at less than 80Amps anyway and maybe even more. I'd slap a demand monitor on the supply for a few days or a week and just warn the customer that they may need to explore load shedding amongst other options if they exceed the demand allowed by the fuse.
 
cheers marvo
nay bad suggestions,when you are a one man band sparky working for your regular customers.its hard to just say installation failed see you.you have to come up with solutions.
 
sub main feeds into one building then from that to next building.dont really want to dig up cable in ground.
 