I have a friend that has had two Commercial Fridge counters installed each with a compressor that has a max operating current of 16A. The company that has installed them have plugged them into the ring main via extension leads. Should these not be on their own dedicated supplies?? Apparently the compressors keep blowing because there is not enough power on startup. Can anyone help with this?
 
I doubt it. If the compressors are hermetic then they have protection against issues caused by low voltage. It would be a bit iffy plugging them into a ring final circuit with a 13A plug though....do they blow the fuse in the plug?
 
Hi Marvo

I'm not sure, apparently it is the fridge engineers saying that there is not enough power, I will ask the question about the fuses mind. It is a butcher that has put these fridge counters in a "farm shop" Apparently there is a 40v volt drop when these compressors start up....
 
tou will need to find out if this volt drop is a preoblem with the customer's installation or a DNO supply problem before you can tackle it.
 
If the compressors are single phase then the voltdrop momentarily on start-up would be expected. As a rule of thumb a single phase compressor will draw roughly 5 times its run current for a fraction of a second during starting, hence the voltdrop is expected within limits.

Plugging a 16A load into a 13A socket would be bad practice and I'm assuming against the UK regs but if the compressor is starting cleanly ie the start relay isn't chattering and it's not cycling on the Klixon thermal safety or the internal winding thermistor then it's probably not a power issue. These symptoms of low voltage are firstly pretty obvious so the fridge guys would be able to state categorically that it was the cause. Secondly there's sufficient protection installed around the compressor to prevent permanent damage occurring as a result of voltage dips so if compressors have failed I'd be investigating other possible causes as well.

When fridges are rated for maximum current draw it's a worst case scenario where the condenser is blocked and the air temp across the evaporator is high and high external ambient temps. Under normal circumstances a well maintained fridge could be running at 60% of it's rated maximum current or even less possibly so depending what other loads are on the circuit it may or may not be overloaded.
 
From what I can see the sub CU that is supplying the shop is on a 10mm SWA From another 3 phase Board supplied from the main board via a 25mm SWA. Until the compressors kick in voltage is fine.
 
Would imagine the RFC your refrigeration plant is protected by a 32 a cb typeB I would hazard a guess that these cabinets should be on their own dedicated circuit designed correctly and protected by a C type OCPD to allow for inrush on start up, remember these cold cabinets are cycling on and off due to the loading of the chiller, won't do a plug top fuse much good. That's my take anyway.
 

Reply to Refridgeration in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K
Hi, The RCD which protects my 16A ring main always "trips" when I plug/unplug a Laptop power supply. No other type of appliance causes a problem...
Replies
8
Views
3K
I have an at my local scout group. They have employed a company to sand & varnish their hall floor. the company is using a couple of Lagler Hummel...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock