Hello guys, just wanted to ask if its safe to run ring final wires behind central heating pipes that clipped to the wall? I know it might be not a good practise as cables might be hot from central heating pipes, but there is no other way to drop cables down as pipes running all the way along the wall. Please advice guys what would you do in that situation?

Thank you for advice.
 
Hello guys, just wanted to ask if its safe to run ring final wires behind central heating pipes that clipped to the wall? I know it might be not a good practise as cables might be hot from central heating pipes, but there is no other way to drop cables down as pipes running all the way along the wall. Please advice guys what would you do in that situation?

Thank you for advice.
Most of the time it will be just fine.
If you are really worried about it you could run that section in LSZH cable with XLPE insulation which will give you an extra 20C headroom, good to 90C; but probably not necessary as most people run their hot water below 70C nowadays.
 