Hi my learned friends.
Have a 3 phase+N instalation supplyed from DNO's 400A cut out.
Tri rated 185mm taken from there into a 600A isolator then off to a change over contactor (gen backup) in 185mm 4 core SWA. with out going into details of distance run and the full install infomation.(not fully informed myself yet)
I wonder if anyone could give any ideas to why the tri rated and swa seems to be running "over" warm!! Loading is Phase 1= 200Amp, Phase 2=210Amp, phase 3=230 Amp. and N= 70Amp.
well under the rateing of the cables.. Any Idea? Note I havnt been to site myself but have ran out of sencible ideas to answer the question..

Thanks
Ed
 
the cable can be upto 90deg cat running temp. you may think that is over warm, but its normal.
 
As doomed said, look at the terminations. Tri-rated is great but….. Without ferules, lugs or cage conections it’s a menace.
If you look in the industrial & commercial section I’ve got a similar problem terminating 95mm super flexible. But like me it’s an older problem.
 