Surmise you are working on a CU change.
1. Isolate main switch to CU panel and lock 'off"
2. Using a dedicate proving box test your GS38 approved voltage tester for correct operation
3. Remove front cover of CU unit
4. With your pre-tested voltage tester check the voltage LINE to NEUTRAL on load side of switch record result
5. With your pre-tested voltage tester check the voltage LINE to EARTH on load side of switch record result
6. With your pre-tested voltage tester check the voltage EARTH to NEUTRAL on load side of switch record result
7. Carry out sections 4,5, & 6 for supply side of switch
8. Re-check your voltage tester with the same dedicated proving box.
Section 1 & 8 re Proving box, you can replace with proven point of utility, but if your changing a CU then once you turn off the supply the whole installation should be off and there would be no point of utility to test at .