M

m1ck_b87

Hi guys
Take a ring circuit for example and its protected by 32a Mcb and spur off the ring with 2.5mm to feed a socket. Lets just say the ring has 26a flowing through it would that spurred 2.5mm be subjected to the 26a.
 
Would be nice to get a straight forward answer, my mind is telling me no because only the load side of that cable will draw the current
 
correct. the spur will only be subjected to the load that is placed upon it. a bit like this bloody great cross on my back.
 
The answer could be all 3 !!!

if 2 x 13A heaters are plugged into the spur socket then 26a flows through the branch cable
if 1 x 13A heater is plugged in the spur socket then 13a flows........

ah you get the drift
 
The answer could be all 3 !!!

if 2 x 13A heaters are plugged into the spur socket then 26a flows through the branch cable
if 1 x 13A heater is plugged in the spur socket then 13a flows........

ah you get the drift
Thanks
 
Ok brain box biff what if I only plugged in a 13a heater into the ring socket would the current flow one half of the ring or would it flow equally throughout the ring
 