L
Lucien Nunes
The OP touches on various things such as fire alarms, where regs other than BS7671 apply regarding segregation, as with telecoms. But it is not true to say that by definition band I and band II circuits may not share a containment compartment. There are alternative ways of satisfying 528.1, such as the use of insulation for the highest voltage present and the presence of an earthed metallic screen. In some cases EMC requirements will dictate physical distances to achieve reliable data transmission but not always.