14th edition doesn't give a minimum size for TN-C-S specifically, it's 6mm minimum for all earthing arrangementsDoes Table D2M of the 14th Ed actually quote a minimum size of bonding for TN-C-S.
14th edition doesn't give a minimum size for TN-C-S specifically, it's 6mm minimum for all earthing arrangementsDoes Table D2M of the 14th Ed actually quote a minimum size of bonding for TN-C-S.
I suspected something like that the 15th Ed cites consulting with the supplier and with this info you have no idea whether 6.0 was actually correct in the first.Yes, it's 6mm, subject to consulting with the supplier
I suppose there's no reason to suggest that it wasn't done properly in the first place.I suspected something like that the 15th Ed cites consulting with the supplier and with this info you have no idea whether 6.0 was actually correct in the first.
You have no way of knowing. What you must do is follow BS7671 and not some random person from the NICEIC.I suppose there's no reason to suggest that it wasn't done properly in the first place.
Yes this is an often quoted statement promoted by the Best Practice Guides. Thermal damage may not necessarily be visible to the human eye so must be taken with a pinch of salt, as I say BS7671 is what you must follow.Has anyone here seen a bonding conductor thermally damaged? It sounds odd to me.
So we should assume all installations have been wired up wrongly? I don't think so. Everything points to this installation having been correctly done for the regs at the time. And I disagree that you should blindly follow BS7671 without referring to the Onsite Guides, Best Practice Guides, GN3 etc. Plus the NICEIC technical helpline is there for a reason and is the most qualified advice I have at hand so I'm going to follow it. Especially (I don't mind admitting it) if it saves ripping a house apart in the process.You have no way of knowing. What you must do is follow BS7671 and not some random person from the NICEIC.
I actually think it's not really relevant that it may have met the regs in 1966. There weren't as many PEN faults then!So we should assume all installations have been wired up wrongly? I don't think so. Everything points to this installation having been correctly done for the regs at the time.
I agree somewhat that the advice that 'if a conductor hasn't suffered thermal damage then it's ok', doesn't make complete sense.I actually think it's not really relevant that it may have met the regs in 1966. There weren't as many PEN faults then!
Isn't the wider principle that if you are significantly altering an installation, the right thing to do is to ensure the alteration complies with the regs today. BPG1 says this on page 5 before proceeding to give questionable advice.
At the end of the day you are putting your name to an EIC saying it complies with BS7671:2022 (unless you specifically list this as a departure of course, and then it's supposed to offer an equivalent level of protection, so I don't see how that stands up to scrutiny)
Personally, I think the "it will probably be ok" get-out-clause in BPG1 is daft and is exceptionally daft if it's PME, as the point is that with no warning a PEN fault could see the bonding carrying the entire return neutral current. There wouldn't be any signs of thermal damage if it hasn't happened before (as @Aaron b said)
Regarding "ripping a house apart", the regs do allow bonding to be "as close as practicable to the point of entry", and on a couple of occasions I've left original undersized bonding in place and added some new 10 sq mm to the nearest convenient point.
Actually I hadn't. I've taken on board everyone's comments, thank you.Well you had decided the NICEIC is the advise to follow before you came on here as it is the easy option and as long as you feel you are satisfying 132.16 then all well and good.