Selectivity/Discrimination between OCPD (60898's)

Can any one shed some light on this.

For Example a B50 MCB upstream of a B16

To my understanding under short circuit fault currents they are generally going to be disconnecting instantaneously. So we should be looking at let through energy I2t data?... would really appreciate if some one could please elaborate on this and what i am looking for on the charts and graphs.

Hager provides a discrimination graph which i cant exactly work out.

Thanks in advance
 
As no-one has attempted an answer yet, I thought I'd mention that typing your complete question into Google results in (to me) a pretty coherent and apparently technically correct AI response. Try it!
A pic of some of it below;

Discrimination/selectivity tables: https://www.hagerelectro.com.au/files/download/0/37839_1/0/CASCADEANDDISCRIMINATIONTABLES.PDF

IMG_1331.jpeg
 
Last edited:
For short circuit discrimination on B50 upstream of B16 you look at I2t let through of the B16. It has to clear the fault with less energy than the B50 can take without tripping. On Hager graph just find the max kA limit shown for that exact combo
 
Thank you. Really appreciate the information given!

So from this graph am I correct in thinking that selectivity will be achieved between a B16 downstream of a B50 up to fault currents of 0.23kA?
 