Put silicon on the back of the back box and thats it sorted. water can not get to the cables or into the house.
 
I seem to remember something from the 16th edition regs that anything outside the house would require its own earth rod. I have not done the 17th edition yet!
 
Cheers for advise, think i will go for weatherproof fcu also to cut down on internal mess.

Is it ok to have the L N cpc conductors just drilled through the wall as these will only b single insulated?? or do i have to put conduit in the wall?? Robo
Cables will need to be protected,so a bit of pipe through the wall will do
 
A lot of cable manufacturers will also recommend that silicone is NOT used around cables due to reaction with the PVC.
 
Apparently, not only is silicone considered to adversely affect the PVC sheath/insulation, it also doesn`t give as good a seal as many expect - certainly not outside in the cold British winter...like now.

Got to say i regularly do what Jason described - sometimes with a galv box, usually with an IP adaptable one - & feed the still inner pvc sheathed conductors thru PVC conduit in the wall into the back of an FCU. IP FCUs are ridiculously expensive (especially MKs) and the way described works fine anyway - altho it`s easy enough to make up your own IP FCUs cheaply now.

Oh, & in case you weren`t aware Robo, the work`s notifiable :eek:
 
Last edited by a moderator:
Just to confirm, the SWA should be buried 500mm deep (600mm if in a veg patch or similar) and the marker tape should be 150mm deep.
Regards

Down2earth
 