Hi
I have lurked here a while but have never posted before.
I have been to a site this week with a view to put some motors on some gates, however the current installation needs some attention.
The site is a builders yard sited probably 20 meters from a large house the yard is supplied by 10MM SWA from a Pme supply at the house dno sticker on the cut out.
There are a couple of shipping containers converted to storage units converted to storage units. They both have lights and two 13amp sockets.
The containers and the fence posts do not test as extraneous and this was a wet damp day. However I am uneasy about them being connected to the Pme given the new regs possibly meaning a lost pen conductor is not as unheard of as we are led to believe.
My instinct is to disconnect the earth and tt the site with a few rods but do you think there is a valve in keeping the pme earth also.
On my arrival there was no rcd at any end but have swapped main switch in container as had one on the van.
Sorry for long post.
Thanks
Tom
 
Why not just add a local earth spike to the existing PME supply?
I agree. PME / TN-C-S (meaning "protective multiple earth") already has multiple earths, so if you're worried then add another and test to be sure.
 
Hi thanks for the replies.
My concern really with that is could it be considered a temporary installation or possibly like a caravan so frowned upon.

No definatly made of metal but not coming out the ground as such.

Tested to house MET and also some deep Piling shafts presume it was outer casing but was stuck out ground prob ten meters ish away

Thanks. Tom
 
It would be classed as a mobile or transportable unit and is a special location. Section 7 prohibits a TNCS earthing system unless under skilled supervision or a vague reference to confirmation of suitability.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Adlington
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Lancs Electrical

Thread Information

Title
Shipping containers pme
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Tommy2002,
Last reply from
Deleted member 9648,
Replies
7
Views
2,602

Advert

Back
Top