Hello all,
After some advise please!
TN earthing system.
DB1;
Zdb = 0.16
IPF = 0.22 / 1.00kA
Circuit Lodge 1;
100A / 100mA Time Delayed RCD
C80 MCB - Maximum Permitted Zs @ 80% 0.22 Ohms
16x2c Cu SWA
Lodge 1;
Measured Zs = 0.46
Measured Line-Neutral Loop = 0.40
Obviously the high Zs is covered by the RCD for fault protection.
What would I check against for the line-neutral loop? Could I use the generic for the C80 or will I have to find the manufactures curve.
If I am correct;
C80A - Magnetic trip between 5 > 10 x rated so between 400A - 800A
Line-Neutral loop = 0.40 which gives a fault current 575A
Would you leave this as is or potentially look at replacing the C curve or even down rating the breaker.
Do I have to look out for anything else?
Thanks all.