We had the mains go off (were were warned it would be off all day today) so I used the generator that I bought two years ago and rebuilt the diesel engine in a quiet period. I have used it before and its run up and load tested every two months.

All appliances in the house appeared to work as normal, and I didn't consider it had any quirks. That is until I noticed two of the outside lights were flickering. LED bulbs and both lights affected are on a light dependent resistor type of sensor on the gable end that brings them on at dusk and off at first light. There are 4 lights sharing this one sensor and they should have been OFF as it was daylight. Only two flickered. All have similar Wattage LED bulbs in them.

It bugged me so I did a few basic tests and with a normal high impedance multi meter and saw 230 volts between neutral and earth at a few 13 Amp sockets.... Now, whether it was 230V at 1mA or 13 plus Amps I don't know, but it was "concerning".

The gennie has the neutral of its alternator strapped to the chassis, at its alternator output using the factory lugs and factory strap and the chassis has a dedicated 6 foot plus ground rod right by it on 10mm conductor sized cable to the factory welded on chassis grounding bush. The live and neutral of the gennie go to a manual 2 pole transfer switch, break before make of 100 Amp rating, so the incoming mains at the outside wall supply cabinet is fully isolated when the switch is in the generator position.

The 3 core cable from the gennie has live and neutral to the transfer switch and the ground conductor goes to the ground terminals where the incoming cable from the grid has ITS neutral bonded to the supply companies ground. So the gennie has 2 ground points, the earth rod by the gennie itself, and via the supply cable that's about 30 feet long to the supply companies ground at the incoming cable before the meter as well.

When the mains was back up about 1.8 volts AC can be measured at the same 13 Amp sockets between neutral and earth terminals.

What does the panel think the fault might be? The outside lights worked perfectly off the grid when it was back up. Gennie is 22kW single phase, British made, commercial quality with a Perkins 3.3 litre diesel with a single phase only Mecalte alternator.

Thanks, if you've got this far
 
Somehow you have no connection between the house main earth terminal and the generator Neutral point.
Could be anywhere but it is worth checking the generator wiring from alternator to output socket
And of course the lead that connects it to the house.
 
Somehow you have no connection between the house main earth terminal and the generator Neutral point.
Could be anywhere but it is worth checking the generator wiring from alternator to output socket
And of course the lead that connects it to the house.
Thank you for the reply James. This fault has occurred after about 18 months of normal operation. I am 99% sure the wiring from the alternator, the generator ground rod, the neutral to ground strap in the generator cabinet and off to the outside box where the mains supply comes in are good.

What I thought a bit ago is could the transfer switch itself be faulty? I tend to suspect electromechanical things first. It's remarkably stiff in action, although I don't expect a 100 Amp changeover switch to be feather light ;)

There's a 2 pole isolating switch between the meter and the transfer switch so I could test the switch and other circuits with the service mains disconnected and the generator not running.

Can you think of a scenario where neutral through the transfer switch might remain connected to the incoming mains even when switched to the gennie, or if it did not connect to the gennie and the earth was carrying the neutral? I am still pondering that and whether either could give these symptoms... The ground to the consumer unit of course remains connected to the service supply bond between neutral and the supply earth terminals whatever the transfer switch is doing or not doing.

Your reply has been very helpful, I am sure this is something simple, it's just safely identifying what's occurred.

Thanks again.
 
With caution and the house running from the generator.
You should be able to trace the fault by measuring the voltage between generator earth and the neutral point / earth point at the distribution board.
If they are high then you are measuring (fault side) move closer to generator and try again, eventually you should find a point that has zero or just a few volts. You are then measuring to a non faulty part of the circuit.
 
With caution and the house running from the generator.
You should be able to trace the fault by measuring the voltage between generator earth and the neutral point / earth point at the distribution board.
If they are high then you are measuring (fault side) move closer to generator and try again, eventually you should find a point that has zero or just a few volts. You are then measuring to a non faulty part of the circuit.


I poked about today and I believe I have found the issue. There's a 3 core lead made out of the flexible cable theatres use on stages. H07 comes to mind. It's expensive stuff and very durable. I bought a 35 foot length from a company that shall remain nameless and I asked what make of Commando 125 Amp connectors they recommended. They told me they also sold the plugs, sockets and joiners and they would supply the cable to length with them fitted if I got them from them at the same time as the cable itself. I was busy and it seemed expedient to do that.

I found after careful tests with just a multimeter that one plug had neutral and live transposed...

I have rectified this but not had time to test that the problem has been resolved, that'll have to wait until tomorrow. but I guess the symptoms fitted the fault.

Thanks again, this is a great forum with generous members.
 
I poked about today and I believe I have found the issue. There's a 3 core lead made out of the flexible cable theatres use on stages. H07 comes to mind. It's expensive stuff and very durable. I bought a 35 foot length from a company that shall remain nameless and I asked what make of Commando 125 Amp connectors they recommended. They told me they also sold the plugs, sockets and joiners and they would supply the cable to length with them fitted if I got them from them at the same time as the cable itself. I was busy and it seemed expedient to do that.

I found after careful tests with just a multimeter that one plug had neutral and live transposed...

I have rectified this but not had time to test that the problem has been resolved, that'll have to wait until tomorrow. but I guess the symptoms fitted the fault.

Thanks again, this is a great forum with generous members.
For completeness fixing the transposed neutral and live cured the issue as expected.
 