I am in the UK.
We had the mains go off (were were warned it would be off all day today) so I used the generator that I bought two years ago and rebuilt the diesel engine in a quiet period. I have used it before and its run up and load tested every two months.
All appliances in the house appeared to work as normal, and I didn't consider it had any quirks. That is until I noticed two of the outside lights were flickering. LED bulbs and both lights affected are on a light dependent resistor type of sensor on the gable end that brings them on at dusk and off at first light. There are 4 lights sharing this one sensor and they should have been OFF as it was daylight. Only two flickered. All have similar Wattage LED bulbs in them.
It bugged me so I did a few basic tests and with a normal high impedance multi meter and saw 230 volts between neutral and earth at a few 13 Amp sockets.... Now, whether it was 230V at 1mA or 13 plus Amps I don't know, but it was "concerning".
The gennie has the neutral of its alternator strapped to the chassis, at its alternator output using the factory lugs and factory strap and the chassis has a dedicated 6 foot plus ground rod right by it on 10mm conductor sized cable to the factory welded on chassis grounding bush. The live and neutral of the gennie go to a manual 2 pole transfer switch, break before make of 100 Amp rating, so the incoming mains at the outside wall supply cabinet is fully isolated when the switch is in the generator position.
The 3 core cable from the gennie has live and neutral to the transfer switch and the ground conductor goes to the ground terminals where the incoming cable from the grid has ITS neutral bonded to the supply companies ground. So the gennie has 2 ground points, the earth rod by the gennie itself, and via the supply cable that's about 30 feet long to the supply companies ground at the incoming cable before the meter as well.
When the mains was back up about 1.8 volts AC can be measured at the same 13 Amp sockets between neutral and earth terminals.
What does the panel think the fault might be? The outside lights worked perfectly off the grid when it was back up. Gennie is 22kW single phase, British made, commercial quality with a Perkins 3.3 litre diesel with a single phase only Mecalte alternator.
Thanks, if you've got this far
We had the mains go off (were were warned it would be off all day today) so I used the generator that I bought two years ago and rebuilt the diesel engine in a quiet period. I have used it before and its run up and load tested every two months.
All appliances in the house appeared to work as normal, and I didn't consider it had any quirks. That is until I noticed two of the outside lights were flickering. LED bulbs and both lights affected are on a light dependent resistor type of sensor on the gable end that brings them on at dusk and off at first light. There are 4 lights sharing this one sensor and they should have been OFF as it was daylight. Only two flickered. All have similar Wattage LED bulbs in them.
It bugged me so I did a few basic tests and with a normal high impedance multi meter and saw 230 volts between neutral and earth at a few 13 Amp sockets.... Now, whether it was 230V at 1mA or 13 plus Amps I don't know, but it was "concerning".
The gennie has the neutral of its alternator strapped to the chassis, at its alternator output using the factory lugs and factory strap and the chassis has a dedicated 6 foot plus ground rod right by it on 10mm conductor sized cable to the factory welded on chassis grounding bush. The live and neutral of the gennie go to a manual 2 pole transfer switch, break before make of 100 Amp rating, so the incoming mains at the outside wall supply cabinet is fully isolated when the switch is in the generator position.
The 3 core cable from the gennie has live and neutral to the transfer switch and the ground conductor goes to the ground terminals where the incoming cable from the grid has ITS neutral bonded to the supply companies ground. So the gennie has 2 ground points, the earth rod by the gennie itself, and via the supply cable that's about 30 feet long to the supply companies ground at the incoming cable before the meter as well.
When the mains was back up about 1.8 volts AC can be measured at the same 13 Amp sockets between neutral and earth terminals.
What does the panel think the fault might be? The outside lights worked perfectly off the grid when it was back up. Gennie is 22kW single phase, British made, commercial quality with a Perkins 3.3 litre diesel with a single phase only Mecalte alternator.
Thanks, if you've got this far