Good afternoon, I carried out an EICR recently on a HMO and found something that caused concern. I wanted to ask what your opinions were on how to remedy.
From the DNO 100A fuse, there are tails going to henley blocks. From there, one set of tails goes to a consumer unit (All RCBO) for the ground floor which is fine. The other set of tails goes to a small consumer unit (3way). This 3 way unit has no 2P main switch, but two 45A 1P MCBs, one supplying the top floor consumer unit and the other supplying the ground floor consumer unit. Both these consumer units are hager boards with a 30ma RCD main switch. The cable used from this 3 way unit supplying the top and ground floor boards is 16mm2 Twin and earth.
I found the MCB screw for the outgoing live snapped, but still secure, so a failure. I wanted to replace this 3 way board with RCBOs, due to the fact that the twin and earth runs behind the walls etc and not mechanically protected like SWA.
So I was thinking of fitting a Fusebox 3 way board with 100A 2P switch, with 2 x 45A fusebox RCBOs. Does this sound acceptable? Wasn't sure if the 2 rcbos should be double pole also, for isolation purposes. Or because it has the 100A main switch, that is sufficient.
Does anyone have any better ideas to best fit the regulations?
Thank you kindly
From the DNO 100A fuse, there are tails going to henley blocks. From there, one set of tails goes to a consumer unit (All RCBO) for the ground floor which is fine. The other set of tails goes to a small consumer unit (3way). This 3 way unit has no 2P main switch, but two 45A 1P MCBs, one supplying the top floor consumer unit and the other supplying the ground floor consumer unit. Both these consumer units are hager boards with a 30ma RCD main switch. The cable used from this 3 way unit supplying the top and ground floor boards is 16mm2 Twin and earth.
I found the MCB screw for the outgoing live snapped, but still secure, so a failure. I wanted to replace this 3 way board with RCBOs, due to the fact that the twin and earth runs behind the walls etc and not mechanically protected like SWA.
So I was thinking of fitting a Fusebox 3 way board with 100A 2P switch, with 2 x 45A fusebox RCBOs. Does this sound acceptable? Wasn't sure if the 2 rcbos should be double pole also, for isolation purposes. Or because it has the 100A main switch, that is sufficient.
Does anyone have any better ideas to best fit the regulations?
Thank you kindly
Attachments
-
WhatsApp Image 2026-03-20 at 13.44.41 (2).jpeg198.8 KB · Views: 69 -
WhatsApp Image 2026-03-20 at 13.44.41 (1).jpeg143.7 KB · Views: 58 -
WhatsApp Image 2026-03-20 at 13.44.41.jpeg236 KB · Views: 55 -
WhatsApp Image 2026-03-20 at 13.44.40.jpeg131 KB · Views: 57 -
Screenshot 2026-03-20 134648.jpg51.5 KB · Views: 51 -
Screenshot 2026-03-20 134624.jpg12.1 KB · Views: 55