I recently put a small 4 way db in a out building fed via a 6mm swa from the house db and i used the job as my annual inspection for napit the inspector said i couldnt use the earth from the house to supply this board without permission from the dno and would have to put in a earth rod even though it had a perfect ze, is this bs or have i missed something?
 
methinks inspector needs to go back to school.
 
What rule or regulation did he quote to back this up?

i take it then that due to his thinking you failed your assessment?

- - - Updated - - -

What rule or regulation did he quote to back this up?

i take it then that due to his thinking you failed your assessment?
 
he didnt fail me he just noted it down that a rod was required and he couldnt find it in the regs hence why i think bs

Why not challenge the guy, you should be knowledgable enough to make him see your installation is fine. I know if it were me I would be straight at him telling him it's fine and backing it up also.
 
Another **** who probably was a mate a couple of years back and now employed as a scammer assessor from the fact he is good as a seller and can bring in the cash lol.
 