You say as part of a project team and also use the term Qualified Electrician too...
Was this a skills course teaching practical skills that should have been overseen by a competent person?
The term Qualified Electrician means nothing on its own, competent is the term one is looking for nowadays.
I personally wouldn't worry if the cable does need replacing either, you are not the designer or installer of this mess you are merely passing on your concerns and possible remedies to resolve them, if it does indeed need digging up then that will fall on the original designer and/or installer.
I don't know. It was a new build and managed by external project manaf=ge
Use the palm of your hand, its cheaper and instant results, the issue is any heat build up may not be constant but intermittent and it may come down to the fact you check it at the wrong time to get any real feedback..
Just look at the cable terminations, gauge its size and calculate its suitability for the job with all cable factors included, you need not go into testing or the like to establish this is a poor/dangerous install.
Ok. Cheers. BTW what's the normal life expectancy of these MCBs. These have been in service for just over 4 years. Reason I ask is because one of the wall sockets on a circuit off the main CU overheated and actually melted and I would have thought the associated MCB would trip before it got to that point. It didn't. So I am wondering whether to recommend replacing at least the ones I suspect might be malfuntioning. That's another issue with this install. It is very difficult not to overload the socket curcuits off the main CU. There are 16 x 13 amp outlets and only 3 x 32 amp MCBs. Total potential load is 208 amps. Like I said. Bewildering.