Over 2 years ago I installed Power to a summerhouse. Yesterday I got a text with a picture of a burnt cable. The job was checked/signed off and passed for my first year of Part P registration.

The cable in question was the live link (4 inches long) between the 45A switch and 40A fuse, load side, in a metal clad box under the stairs. I split the supply. 63A 30ma main switch at summerhouse. Nothing major electrically.

My first thought is arching loose/bad connection. No other cable is affected.

Also the switch did not trip when cable overheated. Had to be turned off manually, must be faulty?

Any other ideas?
 
Hi
Over 2 years ago I installed Power to a summerhouse. Yesterday I got a text with a picture of a burnt cable. The job was checked/signed off and passed for my first year of Part P registration.

The cable in question was the live link (4 inches long) between the 45A switch and 40A fuse, load side, in a metal clad box under the stairs. I split the supply. 63A 30ma main switch at summerhouse. Nothing major electrically.

My first thought is arching loose/bad connection. No other cable is affected.

Also the switch did not trip when cable overheated. Had to be turned off manually, must be faulty?

Any other ideas?

Presumably you signed it off. Loose neutral probably
 
Also the switch did not trip when cable overheated. Had to be turned off manually, must be faulty?

The 'switch' shouldn't trip. It's not a circuit breaker or RCD. Why do you think it should?

An overheating cable, by itself, won't trip either of these other devices anyway.

Most likely cause is a poor connection to the cable in question or a cable with an insufficient current carrying capacity installed.
 