hi guys just want some of your thoughts on the best way to do this. walk in sunbed with 50 tubes at 100 w.....fan in bottom at 1kw and a downlight. its already fed from a dual rcd board on a 32 amp mcb,6mm cable and a cooker switch. the sunbed needs moving about 12 mtrs away from the board so my idea is 40 amp mcb...10 mm t+e and a 63 amp fused isolator on the wall near the sunbed.any suggestions welcome.
 
hi guys just want some of your thoughts on the best way to do this. walk in sunbed with 50 tubes at 100 w.....fan in bottom at 1kw and a downlight. its already fed from a dual rcd board on a 32 amp mcb,6mm cable and a cooker switch. the sunbed needs moving about 12 mtrs away from the board so my idea is 40 amp mcb...10 mm t+e and a 63 amp fused isolator on the wall near the sunbed.any suggestions welcome.


i cant see a need to upgrade cable size :S or breaker
 
why do you want a fused isolator when you have a 40A MCB as OCPD?
 
I just thought because of the distance its going to upgrade cable size....and the isolator is just for maintainence purposes
 
50x 100 = 5000watts 21.5amps
1kw fan 4 amps
light .2 of a amp

not even pulling a load a 7.5kw shower would
 