Supply type to outbuilding question

House supply TN-S with a brick built garage 15m away, property is due a rewire.

Would you keep the garage on TN-S as per the house, which would be a lot easier as they want to have external lighting on the garage, controlled both locally and from the house,

or

To future proof the installation should the DNO convert the supply type when repairing street cabling for example, make the garage TT and then use wireless external lighting and switching controls between the house and garage.

What's your advice?
 
The DNO would not notify of a change from TN-S to TN-C-S. The service cut-out may look like TN-S, but the joint in the street may have been altered to TN-C-S. Unless you know for certain that your supply is TN-S. It may be a better option to use a TT earth instead of the earth in the TN-S submain supplying the garage.
 