Hello there,
I have just started a job that used to be 6 offices which are now being turned into 6 flats. All flats located on the 1st floor. At this moment the meters and switch gear for all 6 flats is on the ground floor in the electrical cupboard. The 25mm tails for each supply go from the meter and terminate into a 60amp switch fuse. From the switch fuse a 16mm twin and earth cable is running up a riser into each respective consumer unit. Each flat will have a 9kw boiler 45amp MCB, 6kw cooker 32amp, sockets, lights, smoke alarm. So I have a few questions I would be very greatful if someone could help me with.

1.) Is the 16mm twin and earth supplying each flat sufficient for the circuit loads I have stated above? boiler 45A, cooker 32A, sockets 32A x2, lights 6A, smoke 6A?
2.) Is the 60amp switch sufficient for this supply or will I need to change it to a 80amp switch fuse?
3.) Is the 16mm twin and earth protected enough going to each flat or should I strip the all out and run Steel Wired Armoured?

Please help,
Thank you.
 
16mm is border line and not leaving much scope for additions in the future.

I would go for 80amp and 25mm swa. It will be pricey though
 

Reply to Supply worries! in the Australia area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
802
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi Guys, We are undertaking a large development and just want to get some ideas on how others would supply each unit. There will be a rising...
Replies
7
Views
2K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Good afternoon all, I have been asked to look at a problem with a bolted neutral but no one seems to know what exactly is the problem. SSE...
Replies
0
Views
663

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock