SHEATH INTEGRITY TEST
A sheath integrity test (e.g. 1000 V minimum insulation resistance tester) applied between the
outer-most metallic layer and earth can identify after-installation damage to the non-metallic outer
sheath.
The measured value should be read after application of the voltage for 1 minute. Ideally the
measured value should be corrected for temperature to a standard value at 20°C if correction
factors are available. A rough guide is that the insulation resistance decreases to one half of the
value for a 10°C rise in temperature. The cable temperature should be recorded along with the
measured values.
Measured values of Insulation Resistance for the sheath should be greater than calculated
values. Calculated values for new cable range from 1.5 MO/km to 4.0 MO/km @ 20°C for PVC
sheaths and from 120 MO/km to 300 MO/km @ 20°C for PE sheaths. Values are highest for
small cables & thick sheaths and lowest for large cables & thin sheaths. (Factory tests show that
measured values are up to an order of magnitude greater than the calculated values.)
Earth the screens after an Insulation Resistance Test on a sheath for at least 5 minutes before
handling or performing other tests.
If anyone once wants to to say I'm wrong Please do!! I will always suck mi grannys eggs
.
So having said that,in a perfect world,just **** the old cable off.n puter new in.
Please tell me you're not going to ignore that terrible IR result you thought was not so important