Eng54
Take this example for instance, from what i found on a PIR on a village hall recently, 60A switched fuse supplying an old wylex board about 25 meters away
supply from Sw/f was 2x 6mm twin and earth taped together throughout the run. install method C
now i considered this a code 2 deviation, with my arguement being if a conductor was disconnected form one of the cables the supply would still be maintained but the CCC halved and now under-rated (and it was a right old bodge up anyhow)
was that justified in that case you think?
Eng54
Take this example for instance, from what i found on a PIR on a village hall recently, 60A switched fuse supplying an old wylex board about 25 meters away
supply from Sw/f was 2x 6mm twin and earth taped together throughout the run. install method C
now i considered this a code 2 deviation, with my arguement being if a conductor was disconnected form one of the cables the supply would still be maintained but the CCC halved and now under-rated (and it was a right old bodge up anyhow)
was that justified in that case you think?
Are you really being serious here?? You code 2 a paralleled supply cable, just in case one cable may be, ...or become disconnected??
Sorry, i've never heard such a load of old rubbish, not for a long time!!! You could apply that daft philosophy to just about any connected cable on any installation..... Do you apply these too, ....What if, it could, maybe, possible, perhaps??