Hey just wondering if anyone knew the reg number regarding addition protection when the length of tails from the meter to the d.b is greater than 3 meters. Struggling to find it so any help is appreciated.
 
433.2.2 and 434.2.1 in th brb givesreference to the3m, but where areduction in xs area takes place.
 
Think you'll find, that's always been a DNO requirement rather than anything laid out in BS7671!!
 
Think you'll find, that's always been a DNO requirement rather than anything laid out in BS7671!!

Agreed. 433 gives the basis for when you need additional step-down protection, however 433.3.1 gives an opt-out at DNO's discretion (which they never give in my experience, although as was put to me by a meter fitter "when was the last time you saw them come out and check?"....).
 
There are quite a number of people who believe that the DNO's as a matter of course provide protection for up to 3m.
I don't quite understand why they believe such, as it could potentially cost the DNO's quite considerably, and they must realise that the DNO's would not provide something for free, when they have no obligation to do so.
 