Testing query

Hi ,

I’m doing a rp + rn test on a radial socket circuit 6 points in total . I’m using a fluke mft 1662 , I’m getting a reading of 0.61 highest on that circuit which is great, I have live and neutral out of terminals at fuse board and in a connector together and I’m using a kewtech socket to mft adapter to test at sockets

Now I’m getting readings from other sockets not on the circuit in fact every other socket at 168 -177 ohms I can’t figure out why as it should be an open circuit > 2000

Could anyone shed some light on the subject much appreciated
 
Hi ,

I’m doing a rp + rn test on a radial socket circuit 6 points in total . I’m using a fluke mft 1662 , I’m getting a reading of 0.61 highest on that circuit which is great, I have live and neutral out of terminals at fuse board and in a connector together and I’m using a kewtech socket to mft adapter to test at sockets

Now I’m getting readings from other sockets not on the circuit in fact every other socket at 168 -177 ohms I can’t figure out why as it should be an open circuit > 2000

Could anyone shed some light on the subject much appreciated
Is this in Ireland?

Have you checked for erroneous connections between circuits?
 
Yeah it’s in Ireland no I didn’t check for erroneous connections yet but it did cross my mind
Other thing worth checking is whether there are loads connected on the other circuit you are checking, or USB ports. You could just be getting a reading through a load.
 
Other thing worth checking is whether there are loads connected on the other circuit you are checking, or USB ports. You could just be getting a reading through a load.
Yeah there was loads connected in the other circuits so I think that would make sense getting readings from the loads connected , I’m new to testing so finding it out the hard way at the start I had a low IR reading on lightning circuit and I traced it back to the led downlights bringing the reading down wasted quite some time on that ,

Another question how to find a corresponding neutral to a live in a packed board that you can’t get at or see the neutral to properly identify it’s the corresponding neutral . Thanks appreciate any help
 
Yeah there was loads connected in the other circuits so I think that would make sense getting readings from the loads connected , I’m new to testing so finding it out the hard way at the start I had a low IR reading on lightning circuit and I traced it back to the led downlights bringing the reading down wasted quite some time on that ,

Another question how to find a corresponding neutral to a live in a packed board that you can’t get at or see the neutral to properly identify it’s the corresponding neutral . Thanks appreciate any help
Can be awkward in a crowded board where the neutrals and protective conductors aren't in sequence to be fair. But if there are loads on the circuits then you can check the resistance between the phase of the circuit and the disconnected neutrals to see where you are getting a reading. Without loads you could put a link in (obviously with it completely de-energised), but it's going to be a bit of a ball-ache. If possible I would try to trace the cables back in the DB, but obviously don't be putting your hands/arms anywhere near any live parts. (Gauntlets may be an idea if there's no main overcurrent device upstream of the DB to remove power from it.)
 
Another question how to find a corresponding neutral to a live in a packed board that you can’t get at or see the neutral to properly identify it’s the corresponding neutral . Thanks appreciate any help
I came across an interesting suggestion for doing this with the CU on, using a clamp ammeter small enough to get on each neutral wire while they're connected. Don't know how useful/practical this might be for your situation! Sort of the inverse of Risteard's suggestion above, be careful!

Put a load on all circuits in the house (or at least all of the circuits you are interested in)
Clamp the ammeter on a neutral - you should see current flowing due to your load.
Work your way through the breakers until you find the one that switches that current off. Now you have the N associated with that breaker/L.
Repeat the process for the other circuits.

PS. To save electricity (!) you could do the reverse, turn all breakers off, and work your way through turning each on until you find the one that causes current to flow at the meter 🤪.
 
Last edited:
I came across an interesting suggestion for doing this with the CU on, using a clamp ammeter small enough to get on each neutral wire while they're connected. Don't know how useful/practical this might be for your situation! Sort of the inverse of Risteard's suggestion above, be careful!

Put a load on all circuits in the house (or at least all of the circuits you are interested in)
Clamp the ammeter on a neutral - you should see current flowing due to your load.
Work your way through the breakers until you find the one that switches that current off. Now you have the N associated with that breaker/L.
Repeat the process for the other circuits.

PS. To save electricity (!) you could do the reverse, turn all breakers off, and work your way through turning each on until you find the one that causes current to flow at the meter 🤪.
Thanks what I do sometimes is power on only the circuit in fact want to find take all neutrals out of the bar and use my volt pen to find the one that beeps , but problem is sometimes once you’re close enough to the board it beeps anyway so not really ideal
 
Can be awkward in a crowded board where the neutrals and protective conductors aren't in sequence to be fair. But if there are loads on the circuits then you can check the resistance between the phase of the circuit and the disconnected neutrals to see where you are getting a reading. Without loads you could put a link in (obviously with it completely de-energised), but it's going to be a bit of a ball-ache. If possible I would try to trace the cables back in the DB, but obviously don't be putting your hands/arms anywhere near any live parts. (Gauntlets may be an idea if there's no main overcurrent device upstream of the DB to remove power from it.)
Yeah I get what you mean it’s mostly when I get a bad global IR reading that I go looking for said neutral to megger
 
Yeah I get what you mean it’s mostly when I get a bad global IR reading that I go looking for said neutral to megger
Out of curiosity what is the scenario? Are you adding something into an existing DB, or is this for a periodic inspection or something else?
 
It’s for a Periodic inspection
Fair enough. I would just note and code the issue RE: low insulation resistance for the installation, and also note that the neutrals (and protective conductors?) are out of sequence, which is another Rule breach. Might also be worth issuing a Notice of Potential Hazard for the low insulation resistance. But I wouldn't spend time disassembling the installation to establish where exactly if it's going to be difficult. That would come under remedial works for me.
 