Theoretically, with a perfectly balanced load/loading it would be equal to the sum of the instantaneous currents which would be zero.
It is very unlikely that this would be the case since it would rise and fall according to the imbalances pulled by all the various single/three phase loads.
 
I’ve got some drawings of the two main types of distribution transformers (DYn11 and DYn1) and the vector diagrams, earthing arrangements, etc. Also the effect of an unearthed neutral, which can be quite devastating. It blew every PC in an office where I worked.
Give me an hour to find them in my wonderful filing system, it’s a total shambles!

Tony is the man, i will keep my gob shut, so as to not complicate it.:wink_smile:
 
I am thinking if the earth connection is removed from the star point the voltage at the star point will rise above 0 volts, I also think the line voltage will be 230 volts with respect to the star point but this 230 volts may be higher with respect to the ground.

I am not sure how much the star point voltage will float about though.
 
The amount the voltage floats depends on the current being drawn. See the vector diagrams in my post.
 