C
ChrisElectrical88
Been to do a DEICR this morning at a good clients house. All circuits tested out fine, good IRs, then I got to the shower.. IRs just over 1M ohm, then could not achive R1 + R2 or get a Zs, turns out 18 months ago a friend had done a fast electrical course and moved the shower switch for them, left the circuit with no earth and not on a RCD!! Then it gets better... Any other 'electrician' came and swapped the shower 12 months ago and didn't mention anything to her!! And the lid wasn't even on correctly on the shower unit! No certificates from either. Left circuit locked off until I can go back, I bet you £1000 it's Choc blocks in the loft with the earth snipped!!