Im just curious as to peoples thoughts on the following install I seen on a video from an Electrical firm today and they did the following:
Ran power to an outdoor shed by coming off the downstairs ring by coming off one of the sockets with a 4mm 3 core cable to an outdoor socket. They then ran a 4mm armoured cable to the shed and supplied it with sockets and lights i have attached a diagram to make it easier to follow. In my opinion this would possibly cause nuisance tripping due to the outdoor lights possibly having water ingress but also is this acceptable in the regs? You can't spur off a spur due to cable current carrying capacity's which he's obviously done but with the cable being the same or even higher than the breaker where do you stand?

1707345089015.png
 
4.0 SWA will happily carry 32A so there isn't an overload situation. There is no Regulation to suggest you cannot spur from a spur (an Appendix is informative). Strictly speaking the lights are not outside and in any case they should be selected to suit the installation environment and as such water ingress should not be an issue they should however have some form of local circuit protection subject to a maximum of 16A.
 

Reply to Thoughts on this scenario? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi, I have recently moved house and what to replace the garden shed. The shed has some electrics; a double socket with a fused light switch and a...
Replies
8
Views
1K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock