well the top of the henly has an exposed terminal block or should i say had , and the metalic cuboard had no earth connection so touching it to close the door was a tad risky View attachment 10972
It is amazing the quality of the reports out there that are accepted without question.
The number of basic errors is really shocking. Feeling a bit saddened that this can go on.
Just had a look through the first forms in more detail and decided to list the obvious irregularities I noticed straight off.
The fact that these are there really does not encourage you that any results have any validity.
Form one
Ze not tested
PFC not tested
Earthing TNS not TNCS
Form not signed
Date incorrect
Db location not completed
Supply protection not completed
Reference method is 1: singles in conduit in a thermally insulated wall? Non standard, if it is that installation then should be A
IR results =200, really?
Llighting is 1.5 not 1, and, as you say, no earth so no R1+R2 possible.
R1+R2 not applicable to a shower, why not, even if disconnected.
Zs and polarity not checked
Circuit breakers are BSEN60898 not just EN68098
EBADOS not correct terminology EEBADoS I might accept.
Second one
An improvement a bit
Still not signed
Cooker is wired in 10/6 cable not the standard 10/4 and not the 6/4! from before?
Lights improved to 1.5 but still with cpc and R1+R2
RCD really a BS4293 in one way in a board?
RCD results for cooker but not sockets
Third form pretty blank really.
Pah! rubbish.