On a TN-C-S the earth cable actually coming from the ground is about 6mm copper. 542.3.1 of the regs suggest table 54.1 (page 159) that 2.5 copper CAN be used if protected by corrosion by a sheath so the 6mm is fandabbydozy.?
Have I read that correctly..?

The ON-Suite guide suggests 16mm in its diagrams on p.15 of the guide.
 
On a TN-C-S the earth cable actually coming from the ground is about 6mm copper. 542.3.1 of the regs suggest table 54.1 (page 159) that 2.5 copper CAN be used if protected by corrosion by a sheath so the 6mm is fandabbydozy.?
Have I read that correctly..?

The ON-Suite guide suggests 16mm in its diagrams on p.15 of the guide.

Coming from the ground?? Are you sure this is not a TT earth rather than a PME/TNC-S system??

Personally i wouldn't have thought a 6mm main earth conductor would have been connected to a PME supply head by the DNO. Go and check the installation again.....!!!
 
Coming from the ground?? Are you sure this is not a TT earth rather than a PME/TNC-S system??

Personally i wouldn't have thought a 6mm main earth conductor would have been connected to a PME supply head by the DNO. Go and check the installation again.....!!!

What I meant is that the earth is part of the TN system and only a 6mm is coming from it.

Yep, adiabatic equation is our friend but ive had a situation with an assessor regarding the above but still the adiabatic was NOT coming up with the desired result.
 
Last edited by a moderator:
What I meant is that the earth is part of the TN system and only a 6mm is coming from it.

Yep, adiabatic equation is our friend but ive had a situation with an assessor regarding the above but still the adiabatic was coming up with the desired result.

Is your earthing conductor coming from a rod, a service head cut out or clamped to a cable sheath?
 
Re post 8 what sort of situation with the assessor.

If it is TNC-S should you not be looking at table 54.8 and not table 54.1.

You need to confirm the Earthing arrangement to receive advice on this issue!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TN-C-S earth supply.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
se7aq,
Last reply from
tony mc,
Replies
9
Views
1,183

Advert

Back
Top