Hi, testing on a big site at the mains I’m getting 0.06 ohms now I can’t verify if it’s TNS or PME, as the incoming supply comes into a sealed unit with built in meter, the transformer is directly behind, Ze has been taken with all parallel earths in place as unable to disconnect, any way I can find out other than speaking to DNO?

Thanks
 
Hi, testing on a big site at the mains I’m getting 0.06 ohms now I can’t verify if it’s TNS or PME, as the incoming supply comes into a sealed unit with built in meter, the transformer is directly behind, Ze has been taken with all parallel earths in place as unable to disconnect, any way I can find out other than speaking to DNO?

Thanks
Can you get access to the original EIC?
 
Surely there will be an N-E link, but what matters as far as the cert is concerned is whether the cable from that point to the LV DB has a CNE or separate N & E cores?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
TNS OR PME
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Bradley6969,
Last reply from
Lucien Nunes,
Replies
14
Views
1,602

Advert

Back
Top